Question: We have to lay direct buried cables on 480V secondary side of transformer. The cables are multiconductor, with five conductors per phase in parallel. NEC 300.5 states that the minimum cover for direct-buried shall be 24”, but it does not tell about spacing between direct-buried cables.When cables are run in PVC conduits, the PVC conduits can be laid in screened-sand in two vertical layers, and the minimum required spacing between adjacent conduits (both horizontal and vertical) is 7.5”.When we lay cables as direct buried, can we still lay cables in two vertical layers? Also when we lay cables as direct buried, what would be the minimum required spacing between adjacent cables? Thanks

You've highlighted a common challenge in electrical installations: the NEC provides minimum requirements, but doesn't always spell out optimal practices or address every specific scenario. Let's break down your questions

1. Can you lay direct-buried cables in two vertical layers?
The NEC Doesn't Prohibit It

The NEC doesn't explicitly forbid direct burial in multiple layers. However, it
does require that the installation meets all applicable requirements, including those related to mechanical protection, heat dissipation, and identification.

Practical Considerations

Laying cables in multiple layers can be problematic for several reasons:

Heat Dissipation

Multiple layers increase the risk of overheating, especially with high-current conductors like you're using in parallel. Soil acts as an insulator, and closely packed cables in layers can create a thermal bottleneck. You'll need to calculate the cable's ampacity considering the derating factors due to burial depth and proximity to other conductors.


Mechanical Protection

The lower layer is subject to the weight and pressure of the upper layer, increasing the risk of damage from settling, rocks, or backfill.

Future Digging/Maintenance

Multiple layers make it harder to identify and work on individual cables in the future without disturbing others. This increases the risk of accidental damage during excavation.


Recommendation

While technically not prohibited,

laying cables in a single horizontal layer is strongly recommended
unless you can demonstrate (through calculations and potentially soil analysis) that heat dissipation and mechanical protection will be adequate with multiple layers.2. Minimum Required Spacing Between Adjacent Direct-Buried Cables The NEC is Silent on Specific Spacing for Direct-Buried Cables

Unlike conduit runs, the NEC doesn't provide a specific minimum spacing for directly buried cables. This is where engineering judgment and best practices come into play.


Considerations for Determining Spacing



Ampacity Derating

This is the most crucial factor. You
must perform ampacity calculations according to NEC 310.15 and the associated tables. The ampacity tables in Article 310 have notes that require derating for more than one conductor in a raceway or cable in close proximity. Even though they are direct buried you should still apply the same rule and the same tables. Derating is more severe if the cables are close together. You need to use Table 310.15(C)(1) to determine the ampacity adjustment factors based on the number of conductors. The goal is to ensure the cables' operating temperature doesn't exceed their insulation rating, even under full load.

Cable Size and Insulation

Larger cables generate more heat. Cables with lower temperature ratings (e.g., 75°C) are more susceptible to derating than those with higher ratings (e.g., 90°C).

Soil Thermal Resistivity (Rho)

This is a critical factor. Soil's ability to conduct heat away from the cables significantly impacts ampacity. A high rho (poor heat conduction) requires greater spacing or more aggressive derating. A soil analysis should be done to find the real value, and then calculate cable ampacity based on that value.


Burial Depth

Deeper burial generally requires more derating, although it also provides some thermal stability.

Fault Current

While less directly related to spacing, the potential for fault current and the cable's ability to withstand it also plays a role. If a fault occurs, closely spaced cables could experience increased mechanical stress and heat damage.


Future Maintenance

As mentioned earlier, adequate spacing makes future digging and repairs safer and easier.

"Rule of Thumb" Spacing

As a general guideline (and not a code requirement), consider a minimum spacing of at least one cable diameter between cables. This provides some space for heat dissipation and future access. For higher current loads or unfavorable soil conditions, you might need to increase the spacing to two or three cable diameters or more.

Engineering Justification is Key

Whatever spacing you choose, document your reasoning and the calculations you performed to justify your decision. This is essential for inspectors, future maintenance, and legal protection.

How to Determine Appropriate Spacing & Layering
1. Gather Information



Cable Specifications

Size, insulation type, temperature rating, ampacity.


Load Requirements

Maximum expected current per conductor.

Soil Analysis

Determine soil thermal resistivity (rho). This is critical.


Burial Depth

Confirmed depth in the field.2.

Perform Ampacity Calculations

Use NEC 310.15 and the associated tables. Account for: Soil thermal resistivity Burial depth Number of conductors in close proximity (derating factors from Table 310.15(C)(1)) Ambient temperature correction Iterate: Try different spacings and layer configurations to see how they affect ampacity.3.

Consider Mechanical Protection

Assess the risk of damage from rocks, settling, or future excavation. Consider using a layer of screened sand above and below the cables for added protection.4.

Consult with an Engineer

This is highly recommended, especially for high-current installations. A qualified electrical engineer can perform the necessary calculations, review your design, and ensure it meets all applicable codes and safety standards.5.

Document Everything

Keep detailed records of your calculations, soil analysis, cable specifications, and the reasoning behind your spacing and layering decisions.

In summary:
While the NEC doesn't provide explicit spacing for direct-buried cables, it's critical to ensure your installation meets all other requirements, particularly ampacity and mechanical protection. Single-layer burial is generally preferred for better heat dissipation and easier maintenance. Ampacity derating is the primary factor driving spacing requirements. Soil thermal resistivity is a critical parameter that must be determined and factored into your calculations. Consulting with an engineer is highly recommended for complex or high-current installations.By following these guidelines and documenting your decisions, you can ensure a safe, reliable, and code-compliant direct-buried cable installation. Flag for review